2 Next Author Message srikanthk28Post subject: Operating a Breaker
Posted: Fri Dec 12, 2008 3:45 pmFri Dec 12, 2008 3:45 pm
Joined: Wed Oct 17, 2007 5:20 pm
Posts: 2
What are you recommending your customer when they ask you regarding recommendation on PPE for operating a circuit breaker with covers on.
1. 480V Switchboard / Switchgear
2. 208V UL Panel / Explosion proof panel
3. 480, 208V Disconnects.
An arc-flash study is performed and we are asked regarding whether they have to wear PPE for operating the above equipment.
Need thoughts.
Post subject:
Posted: Fri Dec 12, 2008 6:01 pmFri Dec 12, 2008 6:01 pm
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Yes they do, unless the switchgear is arc rated. That why many companies are doing remote switching and racking
Post subject:
Posted: Fri Dec 12, 2008 6:40 pmFri Dec 12, 2008 6:40 pm
Arc Level
Joined: Thu Jan 10, 2008 8:49 pm
Posts: 520
Location: New England
On the switchgear I would say yes.
On anything that is explosion proof, Class I or II Div 1, then no. The equipment is inherently arc proof and tested to vent any deflagration inside and vent the gas below the auto-ignition of the Class its in. It is not listed as Arc Fault, but if you understand the test requirements to get a listing then you know it can't release a flame.
On circuit breaker panels I think you get a mix of results. Some say that AF is only for exposed live parts, and with 2009 switched high energy change of states like switchgear. I am not sure molded case would fall in the same category. If it is under 240V and fed from less than 125KVA xfrm, then an analysis is not required. The PPE level is not specified, so if you chose -1, tee shirt and jeans, you would be fine. This would also conform to the NFPA table for under 10KA fault current.
Post subject:
Posted: Tue Dec 30, 2008 4:38 pmTue Dec 30, 2008 4:38 pm
Sparks Level
Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
srikanthk28 wrote:
What are you recommending your customer when they ask you regarding recommendation on PPE for operating a circuit breaker with covers on.
1. 480V Switchboard / Switchgear
2. 208V UL Panel / Explosion proof panel
3. 480, 208V Disconnects.
An arc-flash study is performed and we are asked regarding whether they have to wear PPE for operating the above equipment.
Need thoughts.
Some of these questions are controversial. To say PPE is required to operate a breaker on dead front equipment is to say the manufacturer's equipment is not going to stand the rigors of duty it was designed for. I don't think Cutler Hammer or GE will remain quiet indefinitly about that, though at this point I am not aware of any statements they have made.
Post subject:
Posted: Wed Dec 31, 2008 6:36 amWed Dec 31, 2008 6:36 am
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Gary B wrote:
Some of these questions are controversial. To say PPE is required to operate a breaker on dead front equipment is to say the manufacturer's equipment is not going to stand the rigors of duty it was designed for.
Containment of an arc flash was never part of the design, thats why there are new standards for switchgear to be "arc rated"
Post subject:
Posted: Wed Dec 31, 2008 2:06 pmWed Dec 31, 2008 2:06 pm
Sparks Level
Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
Zog wrote:
Containment of an arc flash was never part of the design, thats why there are new standards for switchgear to be "arc rated"
It is a reasonable assumption that "Arc Rated" equipment will help protect personnel, however, to simplify personnel protection to a "yes-no" answer based on equipment designation is dangerous and negligent, overlooking where arc venting is directed or whether the equipment is operated within it's parameters. And yes-no answers based only on equipment designation, do not include probability and consequences that are recognized in NFPA 70E prescriptive tables. Finally, PPE required by NFPA 70E is thermal rated yet arc rated gear has much to do with ballistic type control, to assume protection for one phenomena based on coincidental design for the other is not good science though it might be the best we have.I stand by my statement that this is controversial.I expect there will be further interpretations from the manufacturers of non arc rated equipment in the future, because it would be a liability to sell apparatus that requires thermal protection to operate in the fashion intended.
Post subject:
Posted: Thu Jan 01, 2009 8:39 amThu Jan 01, 2009 8:39 am
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Gary B wrote:
I stand by my statement that this is controversial.
You can say that again. But, you still need PPE for operating switchgear, I have seen dozens of cases when the switchgear failed to contain a fault, ,my point was the manufactures never designed it to contain a fault in the past.
Post subject:
Posted: Tue Jan 06, 2009 10:52 pmTue Jan 06, 2009 10:52 pm
Sparks Level
Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
Zog wrote:
You can say that again. But, you still need PPE for operating switchgear, I have seen dozens of cases when the switchgear failed to contain a fault, ,my point was the manufactures never designed it to contain a fault in the past.
I do not believe it is a requirement to wear PPE to operate some of the equipment listed in the original question. With further analysis one can determine that some non arc rated switchgear may safely be operated according to NFPA 70E without PPE.It sounds like you are selling something
Post subject:
Posted: Wed Jan 07, 2009 10:27 amWed Jan 07, 2009 10:27 am
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Gary B wrote:
I do not believe it is a requirement to wear PPE to operate some of the equipment listed in the original question. With further analysis one can determine that some non arc rated switchgear may safely be operated according to NFPA 70E without PPE.
Gary B wrote:
It sounds like you are selling something
The assumption that the doors will come open has to be made, there is no way (As of now) to calulate the hazards with the doors closed. Too many assumptions of the condition of the switchgear and retention hardware would need to be made.Just safety my friend, I have had some personal experiences with burn units that I dont wish on my worst enemy.
Post subject:
Posted: Thu Jan 08, 2009 7:33 amThu Jan 08, 2009 7:33 am
Joined: Mon Dec 08, 2008 7:13 am
Posts: 26
Location: Quebec, Canada
Hi,
NFPA 70E 2004 was not clear on this point.
NFPA 70E 2009 130.7(C)(9) FPN No1 clarifies this: "The collective experience of the task group is that in most cases closed doors do not provide enough protection to eliminate the need for PPE..."
It's now hard to say anything else to a customer asking that question.
Also, Table 130.7(C)(9) now gives hazard category for operating equipment with covers on or off.
For example, racking in or out a CB from a 600 V swgr with doors open or closed is category 4...
Simply operating LV D.S. or CB with doors closed is category 0.
Post subject:
Posted: Thu Jan 08, 2009 8:32 amThu Jan 08, 2009 8:32 am
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
JPEG wrote:
For more explosion proof panelsinformation, please contact us. We will provide professional answers.
Simply operating LV D.S. or CB with doors closed is category 0.
If the equipment is within the limitations of the tables.
Post subject:
Posted: Thu Jan 08, 2009 5:30 pmThu Jan 08, 2009 5:30 pm
Arc Level
Joined: Thu Jan 10, 2008 8:49 pm
Posts: 520
Location: New England
Correct me where I go astray.
I thought that reference was not specific to "switchgear" but something like high energy change of state. This would of course be switchgear, but why is it not a Size 4 motor starter, or a 2, or even a 0. Where do you draw the line.
Post subject:
Posted: Thu Feb 19, 2009 8:04 pmThu Feb 19, 2009 8:04 pm
Joined: Thu Feb 19, 2009 6:52 pm
Posts: 2
NFPA 70E does provide a flowchart which you can use to help Annx F.1.
There are no calculations for operating a circuit breaker in a panel with covers on. Therefore I do not believe you will see in the text of 70E sny suggestion to do so. Some places figure the door is open for the PPE requirements, I think that is a little exteme, I would rather is that a minimum of cotton clothing and leather gloves be used. But, for larger gear because fault currents and the shape of the cubicles I would require a Arc Rated faceshield, FR clothing and Heavy leather gloves.
Post subject:
Posted: Sat Feb 21, 2009 5:32 pmSat Feb 21, 2009 5:32 pm
Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
The more important question is the enclosure rated to withstand? Which is a tough question, sometimes, to answer.
One would hope that if it came form a UL panel shop and was listed it would be, but field modifications or custom on site fabricated (they do exist) enclosures may not be able to contain the flash/blast.
It is always safer to err on the more stringent side.
Post subject:
Posted: Sat Feb 21, 2009 5:43 pmSat Feb 21, 2009 5:43 pm
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
SirSpark wrote:
The more important question is the enclosure rated to withstand? Which is a tough question, sometimes, to answer.
One would hope that if it came form a UL panel shop and was listed it would be, but field modifications or custom on site fabricated (they do exist) enclosures may not be able to contain the flash/blast.
There is nothing in any manufacturing standard that requires the switchgear to contain an arc flash, no one ever made that promise and if you read the inst book from any OEM's swgr you will see the warnings and disclaimers about this all over it.Now new arc rated switchgear, tested and rated per the new ANSI arc rated switchgear standard is a different story, but besides some of the testing I have witnessed, I have yet to see any of this new gear in place, it is very expensive and not many companies are willing to make the inverstment, buying a flash suit for thier guys is cheaper.
Post subject:
Posted: Sat Feb 21, 2009 5:55 pmSat Feb 21, 2009 5:55 pm
Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
Zog wrote:
There is nothing in any manufacturing standard that requires the switchgear to contain an arc flash, no one ever made that promise and if you read the inst book from any OEM's swgr you will see the warnings and disclaimers about this all over it.
Now new arc rated switchgear, tested and rated per the new ANSI arc rated switchgear standard is a different story, but besides some of the testing I have witnessed, I have yet to see any of this new gear in place, it is very expensive and not many companies are willing to make the inverstment, buying a flash suit for thier guys is cheaper.
Page 8do not open doors unless breaker is tripped....Page 26When the switchgear is energized....door closedPage 27....And yes their is arc resistant gearI may not have been clear in my wording...But I would hope that if the tag on the gear said XYZ AIC that the enclosure should be able to withstand XYZ AIC, it may never function again but it should be able to contain the blast and not cause damage to the surrounding. Note I did not say person.Bottom line nothing can contain a catastrophic failure, hence the term catastrophic.
Post subject:
Posted: Sun Feb 22, 2009 6:25 amSun Feb 22, 2009 6:25 am
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
SirSpark wrote:
I may not have been clear in my wording...But I would hope that if the tag on the gear said XYZ AIC that the enclosure should be able to withstand XYZ AIC, it may never function again but it should be able to contain the blast and not cause damage to the surrounding. Note I did not say person.
AIC rating hasto do witth the switchgear containing the pressures from an arc flash, it is a short circuit interuption rating, you are comparing apples and oranges.My company designs and builds switchgear, and I can tell you unless it is of the Arc-Resistant type and qualified in accordance with ANSI/IEEE C37.20.7 no switchgear will contain an arc flash.This is a very dangerous assumption many people make, thats why arc flash PPE is required for switchgear operations with the doors closed in the 70E tables.
Post subject:
Posted: Tue Feb 24, 2009 4:49 pmTue Feb 24, 2009 4:49 pm
Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
Zog wrote:
AIC rating has nothing to do witth the switchgear containing the pressures from an arc flash, it is a short circuit interuption rating, you are comparing apples and oranges.
My company designs and builds switchgear, and I can tell you unless it is of the Arc-Resistant type and qualified in accordance with ANSI/IEEE C37.20.7 no switchgear will contain an arc flash.
This is a very dangerous assumption many people make, thats why arc flash PPE is required for switchgear operations with the doors closed in the 70E tables.
You are correct...I never said one should not wear the proper PPE...Though one should also always have the doors closed, however this does pose a problem for racking breakers.
Post subject:
Posted: Tue Feb 24, 2009 5:55 pmTue Feb 24, 2009 5:55 pm
Plasma Level
Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
SirSpark wrote:
You are correct...
I never said one should not wear the proper PPE...Though one should also always have the doors closed, however this does pose a problem for racking breakers.
You said the gear should contain the blast, which it probally wont. As far as racking breakers go, thats what remote racking is for. http://www.remoterackingsolutions.com
Post subject:
Posted: Wed Feb 25, 2009 4:10 amWed Feb 25, 2009 4:10 am
Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
I shall be more carefull with my wording...
Though to an extent it will contain the blast, haha, not that it will be functional again.
Points of weakness would be the door hinges and latching mechanisms, causing the door to fly off. I would think.
Display posts from previous:
Sort by
Page 1 of 2,
2 NextYou cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum
Jump to:
These organizations have a (relatively) uniform approach when it comes to actually classifying equipment for use in hazardous areas. Through rigorous testing, a piece of equipment is assigned an area classification, division or zone, equipment group, and temperature class. An example of a Class I area would be an oil refinery, paint shop, or offshore oil rig. A Class II might be a coal mine, grain silo or hay storage facility. Class III would be something like a paper mill, textile mill, or woodworking facility.
Furthermore, a division or zone is assigned to the product. This is a description of the frequency with which the combustible gas and/or dust is present within the hazardous area. Divisions were used in older North American hazardous area standards, while zones are used in European/International standards as well as newer North American Standards.
The newer standards have switched to the use of zones, in part because they break down areas that previously were only described by two divisions into three more precise zones. Zones also have the added benefit of including the area classification with the zone description. Zone 0 describes an area in which a combustible gas will be present continuously while zone 20 describes an area in which combustible dust will be present continuously (the '2' in 'zone 20' indicates dust as opposed to gas).
The equipment group describes the type of hazardous material that is or could be present in the hazardous area. North American and international organizations use different standards to represent the equipment group, but they all describe the same thing: the type of combustible material in the presence of which the equipment can be operated.
Lastly, a device meant for use in a hazardous area is assigned a temperature class. The temperature class is the maximum ambient surface temperature the device can reach (under maximum dust layers where applicable). This rating is given to help prevent combustion based on the combustion point of the material present in the area. This is used to determine the ambient operating temperature of the device. The approved product will also have a maximum ambient operating temperature. Most facilities will want to operate at a maximum of 80% or below of the maximum ambient operating temperature. Some examples of temperature ratings commonly seen on devices are T1 (450°C), T3 (200°C), T4 (135°C), and T6 (85°C). Traditional US and Canadian systems may also include such temperature classes as T2A, T2B, T3C, etc., which indicate more precise temperature ratings.
As mentioned previously, there are several methods by which devices can prevent explosions in hazardous areas. First, an explosion-proof, flame-proof, or powder-filled device is one in which the explosion is contained and extinguished. Second, limiting the energy of the device to a point where combustion becomes impossible even in the presence of a flammable material, effectively removing the ignition source, is known as intrinsically safe or nonincendive. A non-incendive device prevents ignition under normal conditions. An intrinsically safe device prevents ignition in doublefault conditions. Lastly, a device can simply keep the flammable materials out of the electrical or heat producing components through pressurization, encapsulation, oil emersion, fiber and flying protection, or protection by enclosure. The particular protection concept that a device uses is represented by a marking on the device such as AEXd (Flameproof C1 Z1), Ex ia (I.S. CI Z0). These markings can be looked up on tables and charts available online from the various hazardous area approval agencies.
For more information, please visit explosion proof flex.
Comments
0